3. Operation
Remote control connection and test
RT model
Tower model
1 - Check the UPS is shut down and the electrical supply network disconnected.
2 - Remove connector
(5)
by unfitting the screws.
3 - Connect a normally closed volt-free contact (60 Vdc / 30 Vac max, 20 mA max, 0.75 mm² cable cross section)
between the two pins of connector
(5),
see diagram.
Contact open: shut down of UPS
Contact closed: start-up of UPS (UPS connected to the network and network energized)
Note:
local On/Off control via button
(27)
has priority over the remote control order.
Contact open: shut down of UPS
To return to normal operation, deactivate the external remote shut down contact and
restart the UPS using button
(27)
.
4 - Plug connector
(5)
into the back of the UPS.
5 - Connect and restart the UPS according to the previously described procedures.
6 - Activate the external remote shut down contact to test the function.
Warning: this connector must only be connected to SELV (Safety Extra Low Voltage) circuits