![background image](/i/eaton/99050/eaton-ex-2200-rt2u-netpack-68411/h/eaton-ex-2200-rt2u-netpack-68411-014.png)
34007776EN/AD - Page 12
2. Installation
HotSwap MBP-module operation
UPS start-up with the HotSwap MBP module
1 - Check that the UPS is correctly connected to the
HotSwap MBP
module.
2 - Set switch
(53)
to the Normal position.
3 - Start the UPS by pressing the ON/OFF button
(27)
on the UPS control panel.
The load is supplied by the UPS.
LED
(51)
"UPS ON - OK to switch" on the
HotSwap MBP
module goes ON.
HotSwap MBP-module test
1 - Set switch
(53)
to the Bypass position and check that the load is still supplied.
2 - Set switch
(53)
back to the Normal position.
2.7 UPS connection without a FlexPDU or HotSwap MBP module
The
HotSwap MBP
module has a rotary
switch
(53)
with two positions:
Normal
-
the load is supplied by the UPS,
Bypass
-
the load is supplied directly by
the AC-power source.
Check that the indications on the name plate located on the back of the UPS correspond to the AC-power source
and the true electrical consumption of the total load.
1 - Connect the supplied cable
(31)
(250 V -
16 A) to the socket
(10)
, then to the AC-
power source.
2 - Connect the loads to the UPS using the
cables
(32)
.
It is preferable to connect the priority loads
to the four outlets marked
(9)
and the non-
priority loads to the four outlets marked
(8)
that can be programmed in pairs (1 and 2).
Connect any high-power devices to the 16
A outlet
(7).
To program shutdown of outlets
(8)
during
operation on battery power and thus
optimise the available backup time, the
EATON communication software is
required.
3 - Fit the connection securing system
(35)
that prevents the plugs from being pulled
out accidentally.
Note.
The UPS charges the battery as soon as it is connected to the AC-power source, even if button
(27)
is not
pressed.
Once the UPS is connected to the AC-power source, eight hours of charging are required before the battery can
supply the rated backup time.
EX 3000 XL: at least one additionnal EXB battery module must be connected to the UPS because it does not have
internal batteries.
Refer to EXB battery module installation manual (doc n° 34008167) for further information about connections.
By-p
ass
Normal
UPS ON - OK to switch
BY
P
ASS SWITCH
51
52
53
10
8
9
31
32
35
7