System Unit
Dimensions
(H x W x D) 8 SFF - 1.7 x 17.1 x 23.9 inches (4.35 x 43.46 x 60.76 cm)
8 SFF - 1.7 x 17.1 x 23.9 inches (4.35 x 43.46 x 60.76 cm)
Weight
(approximate)
Maximum:
(all hard drives, power
supplies, and processors
installed)
32.04 Ib (15kg)
Minimum
(one hard drive, power
supply, and processor
installed)
22.03 lb (10kg)
Input Requirements
(for Standard 460W
PSU, see power
specifications tables for
detail on 460W, 750W
and 1200W power
supplies))
Rated Line Voltage
100 to 240 VAC
Rated Input Current
For 550W Power Supply:
6.7 A (at 100 VAC)
3.3 A (at 100 VAC)
Rated Input Frequency
47 to 63 Hz
Rated Input Power
For 550 W Power Supply:
< 670 W (at 100 VAC),
< 660 W (at 200 VAC),
BTU Rating
Maximum
For 550 W Power Supply:
2201 BTU/hr (at 100 VAC),
2153 BTU/hr (at 200 VAC)
Power Specifications
To review typical system power ratings use the Power Advisor which is
available via the online tool located at URL:
www.hp.com/go/proliant-
energy-efficientOrwww.hp.com/go/hppoweradvisor
- Click on the system
of interest. Example: DL160 Gen9- Follow the instructions of the next
screens.
Power Supply Output
Rated Steady-State
Power
For 550 W Power Supply:
550 W (at 100 VAC),
550 W (at 200 VAC),
Maximum Peak Power
For 550 W Power Supply:
550 W (at 100 VAC),
550 W (at 200 VAC),
System Inlet
Temperature
Standard Operating
Support
10° to 35°C (50° to 95°F) at sea level with an
altitude derating of 1.0°C per every 305 m
(1.8°F per every 1000 ft) above sea level to a
maximum of 3050 m (10,000 ft), no direct
sustained sunlight. Maximum rate of change
is 20°C/hr (36°F/hr). The upper limit and rate
of change may be limited by the type and
number of options installed. System
performance during standard operating
support may be reduced if operating with a
fan fault or above 30°C (86°F).
Extended Ambient
Operating Support
For approved hardware configurations, the
supported system inlet range is extended to
be: 5° to 10°C (41° to 50°F) and 35° to 40°C
(95° to 104°F) at sea level with an altitude
derating of 1.0°C per every 175 m (1.8°F per
every 574 ft) above 900 m (2953 ft) to a
maximum of 3050 m (10,000 ft). The
approved hardware configurations for this
system are listed at the URL:
www.hp.com/go/proliant/ashrae
QuickSpecs
HP ProLiant DL160 Generation9 (Gen9)
Technical Specifications
DA - 15031 Worldwide QuickSpecs — Version 1 — 9.9.2014
Page 34