System Unit
Dimensions
(H x W x D)
(with bezel)
6.88" x 17.48" x 29" (17.5cm x 44.4cm x 73.6cm)
Weight
(approximate)
Maximum
(all hard drives, power
supplies, DIMMs and
processors installed)
116.56.0 lb (52.87 kg)
Minimum
(one hard drive, two
power supplies, four
DIMMs, and two
processors installed)
70.94 lb (32.18 kg)
Input Requirements
(per power supply)
Rated Line Voltage
100 - 120 VAC (1200W PS only)
200 - 240 VAC (1200W & 1500W PS)
Rated Input Current
9.2A (100 VAC), 6.6A (200 VAC) - 1200W
PS8.3A (200 VAC) - 1500W PS
Rated Input Frequency
50 to 60 Hz
Rated Input Power
1000 W (120 VAC), 1320 W (230VAC)
- 1200W PS
1652 W (at 230 VAC) - 1500W PS
BTU Rating
Maximum
3408 BTU/hr (120 VAC), 4500 BTU/hr (at 230
VAC) - 1200W PS5637 BTU/hr (230 VAC) -
1500W PS
Power Specifications
NOTE:
To review typical system power ratings use the HP Power
Advisor which is available online located at url:
http://www.hp.com/go/proliant-energy-efficient
or
http://www.hp.com/go/hppoweradvisor
- Click on the system of interest. Example: DL580 G7
- Follow the instructions of the next screens.
Power Supply Output
(per power supply)
Rated Steady-State
Power and Maximum
Peak Power
800 W (100 VAC low line),900 W (120 VAC
low line), 1200W (200 - 240 VAC) for 1200W
PS
1500W (200 - 240V) for 1500W PS
System Inlet
Temperature
Operating
10° to 35°C (50° to 95°F) at sea level with an
altitude derating of 1.0°C per every 304.8 m
(1.8°F per every 1000 ft) above sea level to a
maximum of 3048 m (10,000 ft), no direct
sustained sunlight. Maximum rate of change
is 10°C/hr (18°F/hr). The upper limit may be
limited by the type and number of options
installed.
System performance may be reduced if
operating with a fan fault or above 30°C
(86°F).
Non-operating
-40° to 70°C (-40° to 158°F). Maximum rate of
change is 20°C/hr (36°F/hr).
Relative Humidity
(non-condensing)
Operating
10% to 90% relative humidity (Rh), 28°C
(82.4°F) maximum wet bulb temperature, non-
condensing.
Non-operating
5 to 95% relative humidity (Rh), 38.7°C
(101.7°F) maximum wet bulb temperature,
non-condensing.
QuickSpecs
HP ProLiant DL580 Gen9 Server
Technical Specifications
DA - 15187 Worldwide QuickSpecs — Version 2 — 8.17.2015
Page 48